You can learn more about what kind of cookies we use, why, and how from our Privacy policy. If you hate cookies, or are just on a diet, you can disable them altogether too. Just note that the Freshdesk service is pretty big on some cookies (we love the choco-chip ones), and some portions of Freshdesk may not work properly if you disable cookies.
We’ll also assume you agree to the way we use cookies and are ok with it as described in our Privacy policy, unless you choose to disable them altogether through your browser.
Hello,
I would like to command an action from the ESC3-SL controller using a CAN frame. For example to trigger the precharge or obtain the value of an output. Do you have any examples of CAN frames that do this?
here's a screenshot of the frames I see on the CAN bus, they come from communication with the display
Attachments (1)
Capture d_27....png
88.3 KB
0 Votes
4 Comments
Jiri Lambor posted 3 months ago Admin
Hi Brice
There must be an issue, if the Lynx is booting into mode 0 - STOP. It should boot to mode 100 - STANDBY in default. If you want to have PIN at start check this article
Jirka
0 Votes
Brice Le Rousseau posted 3 months ago
In fact I can now trigger the preload on request CAN as explained in my last topic request on the forum. But the default "MODE_STOP" in the Lynx application is causing me problems because I would like to have the pin lock ("MODE_LOCK") directly when the controller/display is switched on without needing to preload.
0 Votes
Jiri Lambor posted 3 months ago Admin
Hi Brice
I made a mistake in the previous response.
The paramter driver/supply/pchgtim must be set to a higher value than -1 (it is defining for how long the precharge last in ms). Please set higher value e.g. -3000
Let us know, if this work
Jirka
0 Votes
Jiri Lambor posted 3 months ago Admin
Hi Brice
To perform the precharge remote you need to:
I hope this will help you
Jirka
0 Votes